Connection Design - Bolts and Welds in combination - Forum BuildIng Design Experts

Connection Design – Bolts and Welds in combinatio...

Homepage Forums Structures Analysis and Design Technical Forum Connection Design – Bolts and Welds in combination

Connection Design – Bolts and Welds in combination

  • Jonathan Murphy
    Participant

    Hi,

    Does anyone out there know why bolts and welds cannot be designed to share force in a connection? -Per AISC

     

    James Forkan
    Participant

    HI Jonathan,

    I think its because AISC is accounting for the fact that the stiffer connection elements will take more load. welded joints have less deformation capacity that bolts joint and will tend to attract more load before the bolt does. The weld would therefore have to be able to support the load independently it would fail and then the connection would in effect become unzipped.

     

     

Viewing 2 posts - 1 through 2 (of 2 total)